I have an unvented Santon cylinder.

When water is being heated there appears to be a small water drip through the tundish. Is this normal?
 
Sponsored Links
Most unvented cylinders have instructions on them on how to recharge if the air gap has gone, well if its a megaflo. This should stop the drip through the tundish.
 
the fitting that will be dripping is the pressure/temp relief valve, so its either to hot or as already been stated the expansion vessel/ air gap needs topping up.
 
Sponsored Links
Thanks for all your posts.

Can someont explain how I recharge the air gap on the Santon unvented cylinder
 
Close the valve that feeds cold mains water to inlet controls of cylinder. Open a hot tap and leave it open. Wait for water to stop coming out. Leave the tap open. Locate the Schraeder valve on the expansion vessel. Use a mechanical 'pen' type pressure gauge to check the pressure. Pump up to 3 bar if required, with a bicycle pump. Put dust cap back on schrader valve. open cold inlet valve. Close hot tap.

Then, look for any more discharge from the T & P tundish. If it continues, get in a G3 geyser geezer.
 