Hi all, The pressure needle on my boiler spends most of the time at 0! Once the boiler as operated for a while it may rise to 0.5 but still far to low compared to the suggested green zone.

I have tried to work out how to increase the pressure but nothing obvious stands out. On all other boiler I have had there was a handle on the inlet.

Could anybody advise how to resolve this? The rads are getting hot but I am concerned with it operating in the red. Also I have air in a couple of rads. I want to remove this but can not shoft it all with the pressure being so low.

Any advice will be well received. Many Thanks,

Craig
 
Sponsored Links
your boiler may have the optional internal filling kit fitted to it .
you should have a white plastic tee shaped key that is stored in the undertray of the boiler . this is inserted into its slot turned and then you can turn the knob next to it to let in water to between 1 & 1 1/2 bar
do not run it at 0.
 