If someone is using WC either with a Boiler or a Heat Pump in a house with UFH only can you please post the WC curve or curves in use.
 
Sponsored Links
Did a few numbers based on my own (radiator) observations over a few years.

Rads are sized on a T50 basis so a required room temperature of 20C would require temps, flow/return/dT, of 75C/65C/10C at whatever the lowest OAT they were sized to. Most of my own rads would just about deal with a OAT of -10C, consequently I would need to oversize by a factor of at least 2 even with at a OAT of 5C or so and by a factor of 2.5 at a OAT of 0C to enable running with lowish ASHP temps, see attached.
 

Attachments

  • ASHP WC Extract.zip
    18 KB · Views: 3