Just over a year ago I moved into a new house. In around 2001 the previous occupants built a stud partition at the back of the garage in order to form an office. This was all been signed off and approved by the local building control team. Unfortunately they didn't install a door through this stud wall, meaning that we need to walk around the front of the house in order to access the washing machine and dishwasher in the garage. I've now made an application through building control to add a door; obviously a 30 minute fire door given that it is between the garage and the rest of the house. The construction of the stud is 100mm of Celotex sandwiched between 12mm plasterboard.
In modifying the stud wall to add the door I've found that the wiring for the sockets in the wall isn't up to scratch, even for 2001 when it was done. What I initially thought was a ring final turns out to be two radials (there being no link between the final two sockets). It's also clearly a DIY job, with no regard for safe zones and the cables snaking diagonally across the inside of the stud. Finally, I'm pretty sure that the cables are undersized - it's 2.5mm tacked off the 32A MCB that feeds the downstairs RFC. As I understand it the cables will be installed to "reference method 103" which derates the cables to 13.5A given that they are buried between two layers of 50mm Celotex. With a washing machine and tumble-drier plugged in (and potentially running simultaneously) this sounds unsatisfactory.
Oh, as a side note when I took the lid off the consumer unit to verify that the two legs of wasn't an RFC were actually connected to the same MCB I found that the screw had never been tightened up at all - so for 15 or so years the rings feeding the kitchen and garage have been purely 'resting' in the MCB terminal. Phew!
Having consulted the mighty appendix 4 of 7671 I believe the best option here would be "reference method a" (conduit in insulated wall) - which I understand will give me 20A on 2.5mm or 26A on 4mm.
As I see it I have a few choices:
1) Leave things alone, with the cable potentially undersized, and when screwing up shelves in the garage etc run the risk of hitting a cable in the wall.
2) Stick 20mm or 25mm conduit in the wall and re-run the cables through that, keeping them in the zones etc.
3) Replace the 2.5mm with 4mm (potentially in 25mm conduit for good measure), again keeping them in the zones.
Options 1 & 2 reuse the existing cable, which is already connected into the consumer unit. Option 3 would require replacing all of the existing 2.5mm with 4mm, including re-terminating into the consumer unit. Whilst not a qualified sparky I'm perfectly capable of doing the work, though I'm interested in people's opinions of how this fits within part p etc.
* Would 2.5mm in Celotex have been allowed in 2001?
* Assuming that I stick 25mm conduit in the wall and run the cables through this can I get away with reusing the existing 2.5mm?
* If necessary, is replacing the 2.5mm with 4mm a replacement or a "new circuit" (and notifyable accordingly).
* Have I read the tables correctly? Presumably I don't need to apply any grouping factors given it's 2 x T&E in conduit?
Thanks in advance.
In modifying the stud wall to add the door I've found that the wiring for the sockets in the wall isn't up to scratch, even for 2001 when it was done. What I initially thought was a ring final turns out to be two radials (there being no link between the final two sockets). It's also clearly a DIY job, with no regard for safe zones and the cables snaking diagonally across the inside of the stud. Finally, I'm pretty sure that the cables are undersized - it's 2.5mm tacked off the 32A MCB that feeds the downstairs RFC. As I understand it the cables will be installed to "reference method 103" which derates the cables to 13.5A given that they are buried between two layers of 50mm Celotex. With a washing machine and tumble-drier plugged in (and potentially running simultaneously) this sounds unsatisfactory.
Oh, as a side note when I took the lid off the consumer unit to verify that the two legs of wasn't an RFC were actually connected to the same MCB I found that the screw had never been tightened up at all - so for 15 or so years the rings feeding the kitchen and garage have been purely 'resting' in the MCB terminal. Phew!
Having consulted the mighty appendix 4 of 7671 I believe the best option here would be "reference method a" (conduit in insulated wall) - which I understand will give me 20A on 2.5mm or 26A on 4mm.
As I see it I have a few choices:
1) Leave things alone, with the cable potentially undersized, and when screwing up shelves in the garage etc run the risk of hitting a cable in the wall.
2) Stick 20mm or 25mm conduit in the wall and re-run the cables through that, keeping them in the zones etc.
3) Replace the 2.5mm with 4mm (potentially in 25mm conduit for good measure), again keeping them in the zones.
Options 1 & 2 reuse the existing cable, which is already connected into the consumer unit. Option 3 would require replacing all of the existing 2.5mm with 4mm, including re-terminating into the consumer unit. Whilst not a qualified sparky I'm perfectly capable of doing the work, though I'm interested in people's opinions of how this fits within part p etc.
* Would 2.5mm in Celotex have been allowed in 2001?
* Assuming that I stick 25mm conduit in the wall and run the cables through this can I get away with reusing the existing 2.5mm?
* If necessary, is replacing the 2.5mm with 4mm a replacement or a "new circuit" (and notifyable accordingly).
* Have I read the tables correctly? Presumably I don't need to apply any grouping factors given it's 2 x T&E in conduit?
Thanks in advance.