Had some gates fitted late last year and the contractor hit the cable which
feeds my outside plug socket and garden lights. Whoever installed the garden
lights connected a normal PVC twin core and earth to the junction box which
feeds the detached garage (by SWA), routed it under my path, then up onto my
fence. The cable is housed in tubular plastic conduit (about 1" diameter)
whilst on the fence and goes to a mini RCD, which then feeds the plug and
lights.

Basically, I want to replace this 'broken' cable between the exterior JB and
the fence.

My questions are:-

1) Was going to use SWA but have seen mention of Hi-Tuf.. Can this be
buried? Need to bury the cable under my path for about 3 feet.

2) I don't want to replace the entire cable length to the outdoor RCD, but
want to join the cable on the fence with a weatherproof JB. How do I get a
watertight connection between the plastic conduit on the fence and the new
JB which I will be adding to join the new / old cable?

Thanks
 
Sponsored Links
How do I get a watertight connection between the plastic conduit on the fence and the new JB

That bit isn't difficult. You get a conduit box with two inlets and a gasket for the lid. If it's in a vertical run, use solvent weld on the upper joint but leave the lower one push-fit to allow for expansion. (PVC has a very high coefficient of thermal expansion).

The problem is this:

then up onto my fence

You shouldn't put mains power on a fence. Think what would happen if it blew down! :eek: :eek: :eek:
 
1) Was going to use SWA but have seen mention of Hi-Tuf.. Can this be
buried? Need to bury the cable under my path for about 3 feet.
Very unfriendly stuff - SWA is much easier to work with. If you bury Hituf it will still need earthed mechanical protection.

2) I don't want to replace the entire cable length to the outdoor RCD,
You don't always get what you want. Replace it all.
 
Sponsored Links
How do I get a watertight connection between the plastic conduit on the fence and the new JB

That bit isn't difficult. You get a conduit box with two inlets and a gasket for the lid.

Even better, a trouser box. But even better than that, I'm going to agree with Ban....No joint at all!!
 