I am soon to invest in a Worcester Bosch 15ri Condensing boiler. Since before hand, I need to add four rads to the existing 8kw (total) rads and replace 1 rad; it seems sensible to account for the new condensing boiler in the calculations for these new radiators.
There was no easy way to get excel to import into this posting format (you've escaped!) so in very rough terms to demonstrate the process used (so it can be critisised)
CH loss calculations - in excel.
Room || Loss W hr || RAD Rated Watts || / 0.6 **to allow for lower temps see notes below**
A || 946w || 1699w || 1019w
B || 1049w || 1230w || 1137w
C || 2485w || 4533w || 2719w
etc totals..
losses 10.97kw - so house is cold at the moment due some rads being too small and not enough heat in the right places.
Emitters 18.17 @ 50 differential - which they are rated at when sold.
Actual yield 10.90kw due - 38 degree differential as per notes.
Tank - number X power pr l X difference / three hour reheat.
Litres = 166 X 1.16 watts X 56 / 3 = 3.59kw
Total KW 14.18 "This is the required boiler size, unless I can improve insulation = 15KW"
There was no easy way to get excel to import into this posting format (you've escaped!) so in very rough terms to demonstrate the process used (so it can be critisised)
CH loss calculations - in excel.
Room || Loss W hr || RAD Rated Watts || / 0.6 **to allow for lower temps see notes below**
A || 946w || 1699w || 1019w
B || 1049w || 1230w || 1137w
C || 2485w || 4533w || 2719w
etc totals..
losses 10.97kw - so house is cold at the moment due some rads being too small and not enough heat in the right places.
Emitters 18.17 @ 50 differential - which they are rated at when sold.
Actual yield 10.90kw due - 38 degree differential as per notes.
Tank - number X power pr l X difference / three hour reheat.
Litres = 166 X 1.16 watts X 56 / 3 = 3.59kw
Total KW 14.18 "This is the required boiler size, unless I can improve insulation = 15KW"
House leaks 11 kw per hour and currently the rads input 8.5 kw per hr in the bedrooms, leaving me to add some downstairs to get it right.
I have sized a new condensing boiler against the loss not the total RAD capacity.
*I have read that a condensing boiler should be run with the return below 50 degrees. But Radiators are designed to produce their rated output at a 50 degree temperature differential.
*This means normally the rads are at 80 and the room can be at 30 or below and were getting what we should be or more. However with the condensing boiler in super efficient mode our temperature differntial is only
*70+50/2 - 22 = 38 degrees difference (assuming a room temp of not more than 22 degrees and a 20 degree drop across the rads). So we need to apply a reduction factor as stated by the rad manufacturer of about .6 to *find the rated output.
*Then compare this new output figure against the loss on each room to see if the RAD can cope or is too small.
- What is the correct temperature to run the boiler at? - the manufacturer quotes maximum efficiency at below 30 degrees - yikes.
- Is the principal I have used in sizing the rads ok?
- Have I arrived at the right boiler size?