I've changed my old fusebox for a new consumer unit. I labelled all the wires and put them into the correct mcbs in the new unit with the socket rings, and garage on an rcd. Don't have an electric shower and the general advice seemed to be not to put the cooker on the RCD. I selected the mcbs according to the size of fuse which was in the original fusebox. No problems - everything seems to work as before and the mcbs seem to isolate the correct circuits.
My question is to do with the size of MCB needed for the garage. The fuse was a 30 amp one so I've put it onto a 32 amp mcb. The wire to the garage is 2.5mm 3-core armoured cable. The garage has its own little fusebox with a 5 amp fuse for the lights and a 30 amp fuse for the sockets which are in a conduit round the wall. Is this size of mcb OK for the job even though its just a single wire to the garage?
Also - I see that the earth for the garage is the 3rd wire in the armoured cable plus the armouring all joined together. It's quite a long way to the garage (about 100 feet) so is this a good enough earth or is there anything else I could/should do?
Thanks.
My question is to do with the size of MCB needed for the garage. The fuse was a 30 amp one so I've put it onto a 32 amp mcb. The wire to the garage is 2.5mm 3-core armoured cable. The garage has its own little fusebox with a 5 amp fuse for the lights and a 30 amp fuse for the sockets which are in a conduit round the wall. Is this size of mcb OK for the job even though its just a single wire to the garage?
Also - I see that the earth for the garage is the 3rd wire in the armoured cable plus the armouring all joined together. It's quite a long way to the garage (about 100 feet) so is this a good enough earth or is there anything else I could/should do?
Thanks.