Hi all,
I'm having an extension put in with hydonic UFH and new radiators throughout
So we need to replace the ancient boiler & leaking vented cylinder
We've opted for Vaillant and our contractor recommended the 637 system boiler along with 170L unvented cylinder - however he has done no calculations.
The Vaillant websitegenerically recommends EcoTEC Plus 624 with uniSTOR 180L for my 4 bed Semi but that doesn't account for the extension or UFH.
so I ran some numbers and worked out the house Heat loss at 19.5KW (including air change + 20% warm up factor) with external temp at -5C
The UFH emits 3.5KW
I'm not sure whether to add this on to the 19.5KW for requirements (total 23KW) as UFH would typically start up before CH at which time it would draw much less to maintain its lower running temp.
Even at the full 23KW demand would this indicate that the EcoTEC Plus 624 (24KW) would be sufficient, and run cost-efficiently too? Which matches the Vaillant generic product finder.
Vaillant help desk were unable to quantify just how much more an oversized boiler would cost to run (e.g. running the 637 37KW boiler for 23KW demand)
Would appreciate any advice
Thanks
Darems
I'm having an extension put in with hydonic UFH and new radiators throughout
So we need to replace the ancient boiler & leaking vented cylinder
We've opted for Vaillant and our contractor recommended the 637 system boiler along with 170L unvented cylinder - however he has done no calculations.
The Vaillant websitegenerically recommends EcoTEC Plus 624 with uniSTOR 180L for my 4 bed Semi but that doesn't account for the extension or UFH.
so I ran some numbers and worked out the house Heat loss at 19.5KW (including air change + 20% warm up factor) with external temp at -5C
The UFH emits 3.5KW
I'm not sure whether to add this on to the 19.5KW for requirements (total 23KW) as UFH would typically start up before CH at which time it would draw much less to maintain its lower running temp.
Even at the full 23KW demand would this indicate that the EcoTEC Plus 624 (24KW) would be sufficient, and run cost-efficiently too? Which matches the Vaillant generic product finder.
Vaillant help desk were unable to quantify just how much more an oversized boiler would cost to run (e.g. running the 637 37KW boiler for 23KW demand)
Would appreciate any advice
Thanks
Darems