Hello everyone, hope you can help. I have a Wickes Heat 60 boiler which once or twice a day suffers flame failure. Everything (fan,pump,etc) is running but the "flame failure" neon is on and its not burning.There is no particular logic as to when this occurs either. I have measured the thermistor resistasnce at about 8.36K and dropping with increase in temp- the fault finding chart says it should be at least 14K.
I am no boiler expert so this is as far as I want to go myself with the gas side of it although the electronics wont be such a problem if I know what to look for- does anyone have a clue whats happening here as I don't want to get ripped off so I would like to at least have some idea of wether I am being fed bull manure or not when I get someone in to look at it.
Thanks in anticipation.........
I am no boiler expert so this is as far as I want to go myself with the gas side of it although the electronics wont be such a problem if I know what to look for- does anyone have a clue whats happening here as I don't want to get ripped off so I would like to at least have some idea of wether I am being fed bull manure or not when I get someone in to look at it.