Hi,
I posted the following in the plumbing and central heating section baxpoti kindly told replied to the post and said I might be able to get some further detail about the regs regarding having a boiler in the bathroom. Any further detail on this will be much appreciated
Post:
Hi,
I have a boiler installed in the bathroom above my bath. I'm unsure if corgi will pass an inspection due to its location. However I have been told that if I close the boiler in (i.e. make a cupboard arond it), this is allowed.
Can anyone shead any light on this situation, I need a corgi certificate ASAP, and I am unable to get the boiler moved to another location.
Thanks,
KillaBeez
Reply from baxpoti:
Providing your boiler is a room sealed appliance you can place it in a bathroom.
If your boiler requires mains electricity it cannot go in the zones around a bath refer to BS7671
.... unless the electrical parts are enclosed to the relevant index of protection (IP) and are also inaccessible to a person using the bath, and are accessible only with the use of a key or tool (screwdriver etc)
So building a cupboard around it with a locked door, would meet requirements.
Post in electrics UK for more info
I posted the following in the plumbing and central heating section baxpoti kindly told replied to the post and said I might be able to get some further detail about the regs regarding having a boiler in the bathroom. Any further detail on this will be much appreciated
Post:
Hi,
I have a boiler installed in the bathroom above my bath. I'm unsure if corgi will pass an inspection due to its location. However I have been told that if I close the boiler in (i.e. make a cupboard arond it), this is allowed.
Can anyone shead any light on this situation, I need a corgi certificate ASAP, and I am unable to get the boiler moved to another location.
Thanks,
KillaBeez
Reply from baxpoti:
Providing your boiler is a room sealed appliance you can place it in a bathroom.
If your boiler requires mains electricity it cannot go in the zones around a bath refer to BS7671
.... unless the electrical parts are enclosed to the relevant index of protection (IP) and are also inaccessible to a person using the bath, and are accessible only with the use of a key or tool (screwdriver etc)
So building a cupboard around it with a locked door, would meet requirements.
Post in electrics UK for more info