wire floodlight to existing socket

vw

Joined
2 May 2007
Messages
29
Reaction score
0
Location
Yorkshire
Country
United Kingdom
Hi,

Installing a floodlight with 2*120 lamps outside building. I am going to fit a plug to light and plug it into the socket inside building. Watts = Volts * AMP. 2*120/230 = 1.04amp. so fitting a 3A fuse plug to the floodlight. My questions are:

1. Is this safe to wire floodlight to socket?
2. If so, based on calculation above, is 3A plug OK.

Thanks in advances
 
Sponsored Links
VW, seems abit 'amateurish', can you not bring a feed from your lighting circuit to a switch then to the lamps?, or eevn FCU from ring to switch to lamps?

It would work, but bear in mind your cable will have to be suitable for the conditions anyway.

Ban will probably have other suggestions
 
nothing wrong at all. this is a diy forum. use arctic flex
 
Sponsored Links
Hello Oharaf and Breezer

Thanks for both of you. Your advices are really appreciated.

By the way, if I want to wire floodlight (2*120W = 240W) to socket. Based on my calculation, is this 3A plug OK? Someone said it needs to be 15A for 500W lamp. I really do not want burn the lamp out.

The last question is that if arctic flex cable is OK to run through outside of house (just half meter). The spec of cable is 3 core 1mm2. Is this right?

Thank you so much
 