Wiring an outbuilding

Sponsored Links
You don't need the CU. You could wire the sockets in 6mm and use a FCU for the lighting.
If you install the CU i would use a 20a for the sockets, wired in 2.5mm.

Regards,

DS
 
You don't need the CU. You could wire the sockets in 6mm and use a FCU for the lighting.
If you install the CU i would use a 20a for the sockets, wired in 2.5mm.

Regards,

DS
How many sockets are talking you about? Getting more than one 6mm cable into a socket terminal and/or an FCU might be tricky!
 
Sponsored Links
MK Logic Plus and Hager Sollysta will both take 2x6mm² (a Hager cooker switch will even take 1x16mm² in it's input terminals!)
 
What's the VD on 50m of 6 milli?
http://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html

or

screenshot_989.jpg


365mV/A
 
[whisper]I know! I wondered if the OP had considered VD...[/whisper]
 