Hi
Just need some advice on wiring this particular E15 timer into my existing wiring, as regards regulations. (I'm in Rep. Of Ireland but AFAIK they're very similar to the UK - so hence the posting here).
I have an immersion running from a switch with on/off & sink/bath. The cable to the immersion is 4 core - (Switched Live to Sink/Switched Live to Bath/Neutral/Earth).
The supply to this immersion switch runs from a dedicated 20A MCB in the consumer unit.
The Horstmann instructions say - "Means of disconnection from the supply having at least 3mm contact separation in both poles must be incorporated in the fixed wiring"
So my questions are;
1. I'm assuming the above means a DP switch must be put in before the timer that isolates both the neutral and live? I take it the MCB is only isolating the live. But why the requirement to isolate neutral as well? This would mean adding an additional switch to the fixed wiring. Also this DP switch will *always* be left on anyhow, so what purpose does it have, being as the MCB can isolate the supply to repair/replace the immersion element?
2. I originally meant to just replace the existing switch with the E15 planning not to wire the sink feed as this would be unused and just wire the Live bath feed (for the large immersion element). But what if I did? What's the UK regulations say on this? Is it law to have a DP switch on an immersion? The timer is acting as a DP one surely anyway.
I will probably put in the DP switch before the timer but I just wondered is it actually required in this setup? Any advice is appreciated.
Regards
Just need some advice on wiring this particular E15 timer into my existing wiring, as regards regulations. (I'm in Rep. Of Ireland but AFAIK they're very similar to the UK - so hence the posting here).
I have an immersion running from a switch with on/off & sink/bath. The cable to the immersion is 4 core - (Switched Live to Sink/Switched Live to Bath/Neutral/Earth).
The supply to this immersion switch runs from a dedicated 20A MCB in the consumer unit.
The Horstmann instructions say - "Means of disconnection from the supply having at least 3mm contact separation in both poles must be incorporated in the fixed wiring"
So my questions are;
1. I'm assuming the above means a DP switch must be put in before the timer that isolates both the neutral and live? I take it the MCB is only isolating the live. But why the requirement to isolate neutral as well? This would mean adding an additional switch to the fixed wiring. Also this DP switch will *always* be left on anyhow, so what purpose does it have, being as the MCB can isolate the supply to repair/replace the immersion element?
2. I originally meant to just replace the existing switch with the E15 planning not to wire the sink feed as this would be unused and just wire the Live bath feed (for the large immersion element). But what if I did? What's the UK regulations say on this? Is it law to have a DP switch on an immersion? The timer is acting as a DP one surely anyway.
I will probably put in the DP switch before the timer but I just wondered is it actually required in this setup? Any advice is appreciated.
Regards