I'm planning to put some sockets and new 2 way lighting circuit in my garage, all in surface mounted conduit, I also need to run a earth bond from the CU to the gas pipe entry to the house, the gas is 6 m along the planned conduit run.
The new sockets will be a new circuit fed directly from the CU. The circuits will be checked and connected by a qualified Electrician.
I've been using the guides on TLC-Direct as a reference, but I've some questions:
1.) Is it permitted to splice in a conduit joining box (a round tee box)?
2.) Are the wago push splices (or the lever ones) acceptable?
3.) Due to the layout of the sockets, radial wiring makes most sense. There will be 2 double sockets and 2 singles, one socket will be in the hallway of the house, the other side of the garage wall. The TLC guide says:
Garage is approximately 21m² and hallway is approx 8m², does that mean I could use 2.5mm² cores?
4.) Assuming the worst case regarding cable sizing (from a cable factor point of view), the first 6m of conduit (containing two 90 deg bends) would contain:
2 * 4mm² (L/N) for socket radial = 2 * 43 = Cable Factor 86
1 * 2.5mm² (E) for socket radial = 1 * 22 = Cable Factor 22
3 * 1.5mm² (L/N/E) for lights = 3 * 22 = Cable Factor 66
1 * 10mm² (E) for bonding = 1 * 105 - Cable Factor 105
Total cable factor 279
6m of 25mm conduit with 2 bends has a factor of 333, so I think this is OK, but would like to confirm it.
The conduit continues to a total length of 10m, but the final 4M will not contain the Earth bond so I think that's OK too.
5.) Does my bonding have to be 10mm² or can I use (for ease of drawing through conduit) 6mm² ?
The new sockets will be a new circuit fed directly from the CU. The circuits will be checked and connected by a qualified Electrician.
I've been using the guides on TLC-Direct as a reference, but I've some questions:
1.) Is it permitted to splice in a conduit joining box (a round tee box)?
2.) Are the wago push splices (or the lever ones) acceptable?
3.) Due to the layout of the sockets, radial wiring makes most sense. There will be 2 double sockets and 2 singles, one socket will be in the hallway of the house, the other side of the garage wall. The TLC guide says:
32 A cartridge fuse to B888 or miniature circuit breaker feeding through 4 mm² live and 2.5 mm² protective conductors (or 2.5 mm² and 1.5 mm² if m.i. Cable) to supply a floor area no greater than 75m².
Garage is approximately 21m² and hallway is approx 8m², does that mean I could use 2.5mm² cores?
4.) Assuming the worst case regarding cable sizing (from a cable factor point of view), the first 6m of conduit (containing two 90 deg bends) would contain:
2 * 4mm² (L/N) for socket radial = 2 * 43 = Cable Factor 86
1 * 2.5mm² (E) for socket radial = 1 * 22 = Cable Factor 22
3 * 1.5mm² (L/N/E) for lights = 3 * 22 = Cable Factor 66
1 * 10mm² (E) for bonding = 1 * 105 - Cable Factor 105
Total cable factor 279
6m of 25mm conduit with 2 bends has a factor of 333, so I think this is OK, but would like to confirm it.
The conduit continues to a total length of 10m, but the final 4M will not contain the Earth bond so I think that's OK too.
5.) Does my bonding have to be 10mm² or can I use (for ease of drawing through conduit) 6mm² ?