Hi
Hope someone can help I need to wire the thermostat to my Baxi Duo Tec 28HE boiler but cant figure out the electrical connections
On the Thermostat I have the following

Live
Neutral
LX (common)
L1 (live feed to item to be controlled)
L2 (changeover contact)

I take it the live and neutral come from the fuse spur. but which connections do I use to the boiler?
Many thanks in advance
 
Sponsored Links
L1 and LX AND YEP L N fom fused spur you may find it easier to mount it on a single back box, tip wire the unit first as they are quite fiddly to wire in place.

An donnections 1 and 2 in your boiler . connection 2 of the boiller is the live out
 
Thanks
So am I right in thinking that the live out from the boiler goes to to LX on the thermostat and connection 1 goes to the L1
 
Sponsored Links
L1 and LX AND YEP L N fom fused spur you may find it easier to mount it on a single back box, tip wire the unit first as they are quite fiddly to wire in place.

An donnections 1 and 2 in your boiler . connection 2 of the boiller is the live out

Hi sorry to jump into this conversation but I've got the same stat and boiler. Just to be clear I wire L N from the spur into the stat? Then the 3 core flex from the boiler goes where?

Thanks :)
 
cartman11";p="1865511 said:
Wired as above and all sorted and working fine, thanks for your help

Hi cartman11

Could you assist me in the same issue you had. Where are connections 1 & 2 that you mention? I only have a mains flex coming from the boiler at the minute.

Thanks
 