I know various aspects of this subject have been covered many times before but I have been left confused by the installation instructions received with my new built-in single oven.
Here's its specs quoted directly from the install leaflet:
Model: Logik LBPCKX10
voltage:230-240V
Power: 3200-3500W
Current: 13-14A [don't know how that was calculated as 3500W/230V is 15.2A but that's what it says]
etc .
And here's the install instruction paragraph:
"An approved suitable cable must be connected from the Consumer Unit (main fuse box)and be protected by its
own 30amp fuse or Micro Circuit Breaker (MCB).
The electrician must provide a fused double-pole isolation switch, which disconnects both the line (live) and
neutral conductors, with a contact separation of at least 3 mm incorporated into the fixed wiring. The fused
switch should be fitted to the kitchen wall, and must be placed in an easy accessible position in accordance
with IEE regulations. Connect the fused switch to a junction box which should be fitted on the wall. The ovens
power supply cable can then be connected. Connect one end to the junction box and connect the other end
to the ovens power connection box which is located at the back of the oven. Remove the cover of the power
connection box and install the cable, in accordance with the connection diagram....etc"
My take on this is that as I don't currently have a cooker circuit I should fit a new cooker radial using 6mm^2 cable running to a DP switch above the (worktop as described above) then running to a hard-wirable cooker connection unit below the worktop from where the oven would be connected.
What I don't understand is:
1/ why does the instructions stipulate a 30A fuse/MCB be used when the current drawn should not be above 16A (3500W/230V=15.2A)
2/ What sort of DP fused switch should be used- as fas as I can see the majority of DP fused switches are 13A which wouldn't do for this.
3/ Assuming I can find a DP fused switch somewhere (any suggestions?) and since the rating has not been specified, I'd fit a 16A fuse in this- is this appropriate?
4/ If I can't find a DP fused switch would installing a 16A fuse/MCB at the consumer unit and simply using a 20A or 45A DP unfused switch be just as safe? Is there any advantage in either other than future-proofing possible oven upgrades later.
Any help and suggestions would be greatly appreciated.
Thanks, Nick78
PS a pdf of the install instructions can be found here if they're of any use:
http://www.buyspares.co.uk/images/m...anual lbpckx10_oven_vestel_ib_final110420.pdf
Here's its specs quoted directly from the install leaflet:
Model: Logik LBPCKX10
voltage:230-240V
Power: 3200-3500W
Current: 13-14A [don't know how that was calculated as 3500W/230V is 15.2A but that's what it says]
etc .
And here's the install instruction paragraph:
"An approved suitable cable must be connected from the Consumer Unit (main fuse box)and be protected by its
own 30amp fuse or Micro Circuit Breaker (MCB).
The electrician must provide a fused double-pole isolation switch, which disconnects both the line (live) and
neutral conductors, with a contact separation of at least 3 mm incorporated into the fixed wiring. The fused
switch should be fitted to the kitchen wall, and must be placed in an easy accessible position in accordance
with IEE regulations. Connect the fused switch to a junction box which should be fitted on the wall. The ovens
power supply cable can then be connected. Connect one end to the junction box and connect the other end
to the ovens power connection box which is located at the back of the oven. Remove the cover of the power
connection box and install the cable, in accordance with the connection diagram....etc"
My take on this is that as I don't currently have a cooker circuit I should fit a new cooker radial using 6mm^2 cable running to a DP switch above the (worktop as described above) then running to a hard-wirable cooker connection unit below the worktop from where the oven would be connected.
What I don't understand is:
1/ why does the instructions stipulate a 30A fuse/MCB be used when the current drawn should not be above 16A (3500W/230V=15.2A)
2/ What sort of DP fused switch should be used- as fas as I can see the majority of DP fused switches are 13A which wouldn't do for this.
3/ Assuming I can find a DP fused switch somewhere (any suggestions?) and since the rating has not been specified, I'd fit a 16A fuse in this- is this appropriate?
4/ If I can't find a DP fused switch would installing a 16A fuse/MCB at the consumer unit and simply using a 20A or 45A DP unfused switch be just as safe? Is there any advantage in either other than future-proofing possible oven upgrades later.
Any help and suggestions would be greatly appreciated.
Thanks, Nick78
PS a pdf of the install instructions can be found here if they're of any use:
http://www.buyspares.co.uk/images/m...anual lbpckx10_oven_vestel_ib_final110420.pdf