There appears to be a few posts on Wiser TRV's.
and another on the schieder wiser forum.
I have a system with 9 x smart TRV's fitter Oct 22. All appeared ok but this year spotted some anomalies and I am looking for others who have the same system to try and get some similar testing carried out. Carried out all of the obvious processes, new batteries, recalibration, swapping between radiators etc.
1. at least 3 of the radiators do not fully close.
2. some random openng of valves when not following a schedule
a) Valves not fully closed so heating rooms when not required.
Swapped the Smart TRV head ( STRV) with other radiators and some move with the head, one the same radiator still does not close properly even though a normal manual trv works fine.
b) A room had the schedule turned off ( do not follow) and the radiator just opened the valve and even though the max in the schedule was 20 it was still rising an hour later at 23. No reason for this.
c) Had the system set to Away Mode for testing.
Let the rooms all cool down and then boost one room for 30 mins ( this should only open the one valve as the rest of the sytem is in away mode so none following any schedule.
I could see the radiators that bleed rising and 1 hour later another room fired up for no reason. Not just rising a little and then shutting down but continuous heat to the radiator.
So I am looking for anyone who wants to run similar tests to see if this issue with Strv's not shutting the valve completely is a bigger problem. I do not know how many months this has been going on so wasted energy.
So first test would be to go to Settings>Away Mode>Heating Setpoint Set to a very low temperature 10 degrees
Then go to Automation
Set the system to Away Mode
Wait for the temp to fall in all rooms.
Home
Select the Boost for one room that has a single radiator for 30 minutes.
30 minutes later
Insights
Heat report at bottom of screen
scroll down
Select all rooms.
Now view the graph as only the boosted radiator shoul be rising on the graph.
Happy to make contact directly with anyone that wants to talk about this more and maybe provide a single update for the forum later
Peter
Ridiculous flaw in the Drayton Wiser system
This one is for schedules changing and opening vales at the wrong time.and another on the schieder wiser forum.
Wiser TRV not fully closing
I have a system with 9 x smart TRV's fitter Oct 22. All appeared ok but this year spotted some anomalies and I am looking for others who have the same system to try and get some similar testing carried out. Carried out all of the obvious processes, new batteries, recalibration, swapping between radiators etc.
1. at least 3 of the radiators do not fully close.
2. some random openng of valves when not following a schedule
a) Valves not fully closed so heating rooms when not required.
Swapped the Smart TRV head ( STRV) with other radiators and some move with the head, one the same radiator still does not close properly even though a normal manual trv works fine.
b) A room had the schedule turned off ( do not follow) and the radiator just opened the valve and even though the max in the schedule was 20 it was still rising an hour later at 23. No reason for this.
c) Had the system set to Away Mode for testing.
Let the rooms all cool down and then boost one room for 30 mins ( this should only open the one valve as the rest of the sytem is in away mode so none following any schedule.
I could see the radiators that bleed rising and 1 hour later another room fired up for no reason. Not just rising a little and then shutting down but continuous heat to the radiator.
So I am looking for anyone who wants to run similar tests to see if this issue with Strv's not shutting the valve completely is a bigger problem. I do not know how many months this has been going on so wasted energy.
So first test would be to go to Settings>Away Mode>Heating Setpoint Set to a very low temperature 10 degrees
Then go to Automation
Set the system to Away Mode
Wait for the temp to fall in all rooms.
Home
Select the Boost for one room that has a single radiator for 30 minutes.
30 minutes later
Insights
Heat report at bottom of screen
scroll down
Select all rooms.
Now view the graph as only the boosted radiator shoul be rising on the graph.
Happy to make contact directly with anyone that wants to talk about this more and maybe provide a single update for the forum later
Peter