Hi all,
Has anyone got any suggestions on a problem wiv luke warm water out of a 10 yr old Worcs 24cdi? problem started suddenly a couple of months ago on a mates boiler.
Flow rate is 8ltrs a min. govenor is fine. gas rated..24kw, fine. Gas valve modulates upto 13mb from heating to HW. getting 60ohms on multimeter from connections 1 & 2 (as per troubleshooting) and HW sensor has been changed????
The only things I can think of now is the plate to plate..or board??
can anyone point me in the right direction thanks!!