Worcester 350 CH problem

Joined
5 Jan 2008
Messages
155
Reaction score
2
Location
London
Country
United Kingdom
When I switch the CH on, the boiler fires up and the radiators get hot, however, after a min or so, the pressure gauge rises very quickly from 1.3 to 2 bar at which point the boiler switches itself off and doesn't come back on (unless I switch the whole thing off and re-start. On doing so, the whole cycle is repeated). - By the way, HW is fine.

Just wondering if anybody had any ideas?

Many thanks.
 
Sponsored Links
check out your expansion vessel you will find the info to do that in f a q[/b]
 
why are you starting another thread? we have already told you to check your thermistor and if thats ok its most likely the anticycle delay on the pcb being faulty.
 
Sorry, I should have mentioned that I changed the thermistor but this hasn't helped!

If it were a faulty 'anticycle delay' would the whole PCB require replacing?

Thanks.
 
Sponsored Links
Unless you are clever enough to know which part on the PCB is at fault and repair it!