Worcester Bosch 24i junior problem

Joined
13 Nov 2010
Messages
2
Reaction score
0
Location
Merseyside
Country
United Kingdom
Please Help?

My boiler first thing in the morning is at fault status (red light flashing).

It also looks empty of water on the pressure gauge.

After adding water to 1.5 bar and starting up the boiler. it works fine and pressure gauge reads about 2.5 bar.

Everything seems fine until next morning same problem!

What could be wrong?

Alan
 
Sponsored Links
Expansion vessel needs pumped up. Pressure dropping during the night when the system is cooling down.
 
Anyone got an idea how much it would cost a plumber to repair this problem.

I would not have a go! not gas registered.
 
Just get a footpump on the valve at the top/back of the boiler. Same as a bike/car valve. Pump it up to 1bar. DO it with drain open to boiler. Refill system and hey presto. Nothing easier.
 
Sponsored Links
unless the flexi is blocked, then its a ****. and you also have bomb for a boiler.
 
probably more of a whoosh as one of the many plastic parts splits.
 
I agree, I have one of these boilers and so does a pal of mine. Both had probs on and off. Replacing mine on the 1st DEC with a Remeha Avanta 28c. Can't bl00dy wait!
 