Hi,
Can anyone tell me which figure on the attached for my British Gas (WB) RD537i is the central heating output normally used in comparisons? I think it is 37.1KW @ net 80/60 deg.


IMG_1168.JPG


IMG_1169.JPG


This boiler is 13 years old and other than early day gas valve fault, it's been trouble free and I'm pleased with it.

The issue I have now is that I want to move this boiler into a new utility area to get it out of the kitchen - it's a bit of a beast, but this was largely due ( I think) to solve the low flow rate we have. The new location would mean venting close to a boundary and I therefore need a flume/plume kit to vent it up and angled. Unfortunately WB don't make a flume kit for this boiler, which I found surprising - aren't they all comparable?

So the upshot looks like I'll have to get a new boiler - Can anyone suggest a good replacement of similar performance? I've been recommended an Ideal Logic Plus, but only seems to be 24KW heating.

Thanks
 
Sponsored Links
It is a combi boiler and so the power is related to water heating and not central heating. You have been accustomed to 37 kW and so I would not recommend anything less than a 32 kW boiler.

Your gas registered installer will suggest suitable alternatives.

Worcester were very slow to start selling plume management kits which surprised me.

Unfortunately we are only allowed to use the manufacturer's flue components sold for the specific boiler.

I expect there may well be other flues with the kits which would fit but we are not permitted to use them!

Tony
 
As Tony has suggested, it's highly unlikely that your home needs 37kW of heat. I'd be surprised if it needs even half that. My 4-bedroom 1970s house uses 14kW. To size your replacement boiler, you need to know what your incoming mains flow rate is in litres per minute. You can find this out by timing how long it takes for a bucket of known capacity to be filled by your cold bath tap.

I'd recommend an Intergas ECO RF with 10 year warranty - similar price to the Logic and a much better boiler
 
Sponsored Links
I don't really understand how Combi's work
This diagram may help (not all combi boiler work in exactly the same way, but the principal is the same).

combisystem.png


When hot water is not required, the heated boiler water is pumped through the radiators.
When a hot tap is turned cold water from the mains starts flowing through the secondary heat exchanger.
A flow detector operates the diverter valve so the hot boiler water produced by the primary exchanger passes through the secondary exchanger.
The cold water is therefore heated up.
Because the cold water is travelling relatively fast a considerable amount of heat is required, depending on the flow rate.
For example:
Flow rate 10 litres/minute; temperature rise 35C (say 5C to 40C) will require a heat input of approx 25kW (a rise to 60C would need 38kW).

The central heating requirement is normally much lower -as others have said. You can find out how much your house needs by using Baxi Whole House Boiler Size Calculator.
 
As Tony has suggested, it's highly unlikely that your home needs 37kW of heat. I'd be surprised if it needs even half that. My 4-bedroom 1970s house uses 14kW. To size your replacement boiler, you need to know what your incoming mains flow rate is in litres per minute. You can find this out by timing how long it takes for a bucket of known capacity to be filled by your cold bath tap.

I'd recommend an Intergas ECO RF with 10 year warranty - similar price to the Logic and a much better boiler

We have 15 litres per min at the Garden tap and 22 litres at the road meter (according to the water board) I think this is why we had a high output boiler as we need to run the tap/shower at full to make it worthwhile.
 
We have 15 litres per min at the Garden tap and 22 litres at the road meter (according to the water board) I think this is why we had a high output boiler as we need to run the tap/shower at full to make it worthwhile.

An Intergas ECO RF 36 will do you nicely then
 
13 years and just 1 part changed,if only WB sourced more boilers from Junkers and just re badge them.

Boiler heating output,well your installer can work that out on site.
 
Many of the early worcesters were just re badged junkers products,kind of a good idea.
 