Worcester Greenstar 37 CDi hot water problem

Joined
26 Dec 2009
Messages
3
Reaction score
0
Country
United Kingdom
Ideas please re my just over 2 year old Worcester Bosch Greenstar 37 CDi. After running hot water to a sink or bath, if I want to top up, even after a few mins the water runs cold for quite a while (40secs approx) until it runs hot enough to use. This started about 2 months ago and is getting worse. I'm suspecting the reservoir is'nt working as it should. Everything else works fine.:(
 
Sponsored Links
DIrty system - wasn't cleaned when the boiler was installed.
Your secondary heat exchanger is sludged up. Common as...
 
Thanks ChrisR. Is it something I can do myself. I'm pretty good with plumbing/heating ;)
 
Sponsored Links
has the eco button got turned off,fhe light is on for off

Gordongas you are the man!! That is exactly what was wrong. Thank goodness I didn't take the "strip down and replace option" tee hee Thanks again and if I can be of any help to you please give me a shout. :) :) :)
 