Worcester greenstar danesmoor 12/18 oil boiler

Joined
30 Dec 2023
Messages
15
Reaction score
0
Country
United Kingdom
I have a worcester greenstar danesmoor 12/18 oil boiler. The boiler worked fine last winter but when I tried to turn it on , it will not ignite. The fan comes on and I hear a clicking sound. When the burner is out I do not get a spark, but i do get fuel.
I have tested the photocell and it changes resistance with and without light.
i have checked the position of the electrodes and they appear good - set as per manual
The system has been bled, fuel filter cleaned

Any advice would be great fully received.
 
Sponsored Links
If you're getting fuel but no spark then either a lead has come away from the electrodes, there's a crack in the electrode insulation or electrodes themselves, or you need a new control box
 
Sponsored Links
Thanks for the advice. The manual gives me settings and the last boiler I serviced is still working a year later and isn't sooty.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top