Hello, i'm new here. This is a great forum, i wish i found it sooner!
We have had the above condensing combi oil boiler for nearly two years now - fitted in an unheated detached garage. During the recent cold weather the boiler was running most of the time day and night resulting in excessive temps in the house.
I researched the problem and deduced that i should be fitting a low limit pipe stat on the CH return pipe and wiring it in series with the frost stat.
I got the parts i needed from the local plumbers merchant and set about tracing the wiring circuits of our boiler and controls. We have a drayton timer switch for DHW in the garage and a drayton digistat +2 programmable room stat for CH in the house.
I then realised we had two frost stats wired to the boiler. On reading the boiler manual it says that this boiler needs two frost stats wired with a shared permanent live and the switched live from each stat going to two seperate terminals on the boiler PCB.
I was then confused so decided to call worcester. They said the pcb was designed to be used with a double pole frost stat and because they are no longer available this is why 2 frost stats have to be used. I asked how should i wire up the pipe stat and they said just take out one of the frost stats and replace with the pipe stat.
Ok i thought but this means the two stats are in parallel not in series. I wired it up as worcester recomended and waited for the temp to drop. With a digital multimeter i deduced that even when the return temps were above the 20 deg C i set the pipe stat at, the frost stat was still turning the heating on. Also when the air temp was above 5 deg C and the return temp below 20 deg C the bolier was coming on.
*******s i thought. I have now disregarded worcesters advice and wired the two stats in series (frost stat to pipe stat) with two switched live wires taken from the pipe stat to the two connections on the boiler PCB.
Tested it and it is running flawlessly. Boiler is still frost protected and it does'nt run all bloody night any more. Result.
I believe worcester gave me wrong advice and why did'nt the installer (worcester accredited installer) work out that i would need a pipe stat? Does'nt fill me with confidence really.
Regards, stu
We have had the above condensing combi oil boiler for nearly two years now - fitted in an unheated detached garage. During the recent cold weather the boiler was running most of the time day and night resulting in excessive temps in the house.
I researched the problem and deduced that i should be fitting a low limit pipe stat on the CH return pipe and wiring it in series with the frost stat.
I got the parts i needed from the local plumbers merchant and set about tracing the wiring circuits of our boiler and controls. We have a drayton timer switch for DHW in the garage and a drayton digistat +2 programmable room stat for CH in the house.
I then realised we had two frost stats wired to the boiler. On reading the boiler manual it says that this boiler needs two frost stats wired with a shared permanent live and the switched live from each stat going to two seperate terminals on the boiler PCB.
I was then confused so decided to call worcester. They said the pcb was designed to be used with a double pole frost stat and because they are no longer available this is why 2 frost stats have to be used. I asked how should i wire up the pipe stat and they said just take out one of the frost stats and replace with the pipe stat.
Ok i thought but this means the two stats are in parallel not in series. I wired it up as worcester recomended and waited for the temp to drop. With a digital multimeter i deduced that even when the return temps were above the 20 deg C i set the pipe stat at, the frost stat was still turning the heating on. Also when the air temp was above 5 deg C and the return temp below 20 deg C the bolier was coming on.
*******s i thought. I have now disregarded worcesters advice and wired the two stats in series (frost stat to pipe stat) with two switched live wires taken from the pipe stat to the two connections on the boiler PCB.
Tested it and it is running flawlessly. Boiler is still frost protected and it does'nt run all bloody night any more. Result.
I believe worcester gave me wrong advice and why did'nt the installer (worcester accredited installer) work out that i would need a pipe stat? Does'nt fill me with confidence really.
Regards, stu