After helping building my brothers workshop he's now done the electrics. Please don't shoot me down about Part P, i have explained this several times to him.
He asked me to take a look (i'm not an electrician) to see what I thought. In the workshop he's got an 40A RCD CU, with 6A for lights, 16A for sockets and a 32A feed to his 3hp air compressor (yet to be switched on).
This all seems fine (perhaps higher amp RCD?) but the problem arose when I checked the supply from his house. He's taken this from a spare 32amp mcb on the RCD 63A side of his house CU. This already has 3 x 32A (sockets) and a 50A (shower) on it plus his new 32A for workshop. So here comes the question!
1. Should he increase the house RCD to 80A and change the mcb to the workshop for a much higher rating?
2. He now has 2 RCD at both ends is this bad practise?
3. Would it make sense to remove feed from the house CU, split the tails (there is an isolator switch on the incoming) and have the feed straight down to his work shop. Totally seperate from the house CU.
Any advice much appreciated,
Cheers Zeb
After helping building my brothers workshop he's now done the electrics. Please don't shoot me down about Part P, i have explained this several times to him.
He asked me to take a look (i'm not an electrician) to see what I thought. In the workshop he's got an 40A RCD CU, with 6A for lights, 16A for sockets and a 32A feed to his 3hp air compressor (yet to be switched on).
This all seems fine (perhaps higher amp RCD?) but the problem arose when I checked the supply from his house. He's taken this from a spare 32amp mcb on the RCD 63A side of his house CU. This already has 3 x 32A (sockets) and a 50A (shower) on it plus his new 32A for workshop. So here comes the question!
1. Should he increase the house RCD to 80A and change the mcb to the workshop for a much higher rating?
2. He now has 2 RCD at both ends is this bad practise?
3. Would it make sense to remove feed from the house CU, split the tails (there is an isolator switch on the incoming) and have the feed straight down to his work shop. Totally seperate from the house CU.
Any advice much appreciated,
Cheers Zeb