E
EdwardCurrent
Hello All.
I understand that an RCD/RCBO should be tested 'at source', but given the 'chance' I tested out a friends RCBO with the 'plug in' lead. The EFLI was .5, (triplock), half rated no trip, 1X 21 ms. 5X >40ms.
Would I be correct in thinking, that the contact voltage that arose during the 5X test exceeded the 50v allowance. And that insulation resistance tests should be carried out asap ?
I understand that this shows my lack of testing experience/knowledge but am trying to understand the basics before embarking on a daunting 2391 'max day ' course. It's all too easy for me to 'read' procedures but I know I need much more 'hands on' experience I need.
Respect as always.
Ed