Client calls to say the gas fitter reckons there is something afoot with regards to polarity of an installation. Occupant has also reported getting a shock from the radiator in the bathroom...
Quick live polarity check, all circuits on, does indeed suggest reversed polarity on supply. DB isolated and polarity is correct. Hmmm? Now where is that earthing conductor actually going? It's going nowhere; just pushed behind some panelling.
Turns out there's a phase-to-earth fault on the upstairs lights, but as there is no effective means of earthing this fault does not clear. Worse though, because of the presence of main bonding, not only do the exposed parts of all circuits become live, so do all bonded conductive parts. Now, if these parts were actually extraneous there would be an earth fault path, but as there is a lot of plastic pipe no such path exists.
And, if you follow this, there is as good a reason as any to test before you bond!
Quick live polarity check, all circuits on, does indeed suggest reversed polarity on supply. DB isolated and polarity is correct. Hmmm? Now where is that earthing conductor actually going? It's going nowhere; just pushed behind some panelling.
Turns out there's a phase-to-earth fault on the upstairs lights, but as there is no effective means of earthing this fault does not clear. Worse though, because of the presence of main bonding, not only do the exposed parts of all circuits become live, so do all bonded conductive parts. Now, if these parts were actually extraneous there would be an earth fault path, but as there is a lot of plastic pipe no such path exists.