Htg circuit is UH3 wiring centre for UFH
Had a problem with the pump not running when stat demands heat.
The zone valve opened and I have power on the orange wire firing the boiler, at this point I didn't check the grey wire voltage as I presumed it was permanent live to one side of the aux switch and because the orange had fired the boiler then the operation of the valve was complete.
Concluded that the pump relay was the issue so new wiring centre ordered, but!
went back to the wiring centre and found no volts on the grew wire?
Changed the zone valve and all is well!
Question, if there was no power on the grey where did the orange wire get its power from?
The above raised a second question
I had the honeywell o/heat stat on the hot side manifold pipe that, when operated, would stop the pump.
When I had the above problem (no pump) the boiler pump kept the system running.
I only knew there as a problem because the pump light wasn't on.
What should the o/heat stat shut down?
Thanks
Had a problem with the pump not running when stat demands heat.
The zone valve opened and I have power on the orange wire firing the boiler, at this point I didn't check the grey wire voltage as I presumed it was permanent live to one side of the aux switch and because the orange had fired the boiler then the operation of the valve was complete.
Concluded that the pump relay was the issue so new wiring centre ordered, but!
went back to the wiring centre and found no volts on the grew wire?
Changed the zone valve and all is well!
Question, if there was no power on the grey where did the orange wire get its power from?
The above raised a second question
I had the honeywell o/heat stat on the hot side manifold pipe that, when operated, would stop the pump.
When I had the above problem (no pump) the boiler pump kept the system running.
I only knew there as a problem because the pump light wasn't on.
What should the o/heat stat shut down?
Thanks