During a refurb job, it was required to re-site the existing meter position.
The original installation was connected TT with a spike in ground reading 402 Ohms.
As they were going to renew the overheads we asked for TNC-S and they said should not be a problem.
The meter is on one side of the room and we have new 17th Fuseboard on the other side of the room about 4M away.
Thinking we were getting TNC-S we installed a 63A Double Pole Mcb adjacent to meter fed with 25mm tails and 16mm Earth, and outgoing 16mm 6242Y to 17th FB.
On going back to connect we found note saying 0.37 TNC-S Not Available.
So now the 16mm Sub-main has no Rcd protection, being just over 0.35 you would have thought they would have connected.
I did a test and inspection some time back to a house on a small site that had around 12 dwellings where the reading was 0.40 assume all connected as PME, the installations were installed by the same electrical provider.
Comments anyone.
The original installation was connected TT with a spike in ground reading 402 Ohms.
As they were going to renew the overheads we asked for TNC-S and they said should not be a problem.
The meter is on one side of the room and we have new 17th Fuseboard on the other side of the room about 4M away.
Thinking we were getting TNC-S we installed a 63A Double Pole Mcb adjacent to meter fed with 25mm tails and 16mm Earth, and outgoing 16mm 6242Y to 17th FB.
On going back to connect we found note saying 0.37 TNC-S Not Available.
So now the 16mm Sub-main has no Rcd protection, being just over 0.35 you would have thought they would have connected.
I did a test and inspection some time back to a house on a small site that had around 12 dwellings where the reading was 0.40 assume all connected as PME, the installations were installed by the same electrical provider.
Comments anyone.