No maximum rating for DNO fuse is 100A. To exceed that one would need a set of fuses to split into circuits. I have done it with one massive house we fitted three consumer units and wired to a fuse box and isolator with a 80A fuse to each consumer unit. The fuse box rated 160A three phase so we could configure for three, split or single phase at up to 160A per phase but this is unusual.The arguement for 2 boards is good as loading has the potential to overload main switch.
All the regs actually say is that, for a single-phase supply up to 100A under the control of ordinary persons, switchgear and control gear assemblies should EITHER comply with BS EN 60439-3 OR be a (type tested') consumer unit, the components and protective devices of which comply with BS EN 60439-3.... all consumer units I have seen are rated 100A so that is maximum size of DNO fuse. There are larger distribution units but for a house under the control of an ordinary person a type tested distribution unit is required which is called a consumer unit. ... Clearly it was a standard unit but at the time I was more commercial and had not realised I needed to use type tested equipment in domestic.
I suspect that opinions about this (and about the definition of "a dedicated circuit" {'dedicated' to one oven, or to three ovens?} ) will vary but 12kW worth of ovens only represents an after-diversity load of about 22A, hence easily supplied by one 32A circuit.All 3 ovens are together in a line of tall housings along with a warming drawer. The ovens pull nearly 4kw each and warranty states dedicated circuit.
Fair enough - that's obviously your choice/decision, and there's nothing electrically wrong with what you propose.For the sake of the additional circuits they may as have separate circuits, ovens cost 700+ each so whats the point faffy around if warranty is called upon.
Fair enough!ovens are going to be in 6mm for that very reason, apart from i have a 100m drum of the stuff that a customer gave me as i present![]()
We don't know that he is self-certifying through his scheme membership (I thought that they'd all dropped the defined/full-scope idea though?).You may well be competent to do the work - I obviously having no way of knowing. However, as has been said, even if competent, you would not be able to self-certify a CU change unless you had full scope membership of a self-certification scheme.
Again, fair enough. All of this discussion has only really about possible ways of reducing the number of ways needed in your CU(s)!That would work but due to the CU being directly above the ovens I'll just have all 3 direct to there mcbs
That's true, which is why I asked the question ...We don't know that he is self-certifying through his scheme membership ...
Are you a member of a self-certification scheme which would enable you to self-certify a CU change?
However...Yes I can self certify it ...
Maybe, but would not the (electrical) scope of that notification be restricted to work related directly to the (notified) extension, not replacement of a house-wide CU?The extension will have been notified, so the electrical work probably doesn't need self-certification.
NaahAll of this discussion has only really about possible ways of reducing the number of ways needed in your CU(s)!
Depends how the work was described. If the extension means extra circuits and a larger CU is needed, then...Maybe, but would not the (electrical) scope of that notification be restricted to work related directly to the (notified) extension, not replacement of a house-wide CU?
As you say, it depends upon what was described. However, it looks to me as if the OP's proposals may well include new circuits which are nothing to do with the extension, and I would not have thought it very likely that such things would have been described in a notification relating to the extension. However, only he can tell us that.Depends how the work was described. If the extension means extra circuits and a larger CU is needed, then...