Yes, of course. Not only does it 'make sense', but I personally strongly believe that is should be 'the requirement'.Probably not a formal requirement but it makes sense to use the worse case voltage to ensure that the instalation is safe at that voltage.
The situation we have is, in my opinion, totally ridiculous and completely unlike what I am used to in the safety-critical world in which I usually operate...
... it is (again 'IMO') ridiculous that if, given a resitive load that draws a current of, say, 29A at 230V, an OP proposing to use a cable with a CCC of 27A woul;d be told that that was 'unacceptable', possibly that it would be 'unsafe' and certainly that it would be 'non-compliant with regulations, yet if the calculated current (at 230V) were 26.5A, we would say that was (just) 'OK', even though the current drawn through the cable would more than 29A (29.15A) if his supply voltage happened to be 253V ! Why is putting 29A (or more) through the cable acceptable, safe and 'compliant' in one of those situations but unacceptable, possibly unsafe and 'non-compliant' in the other ??
Put simply (and 'obviously') safety critical calculations should be undertaken in relation to 'worst-case scenarios', not a scenario which probably exists in less than half of cases!
I would think that well over half the installations in the UK have (at least sometimes) a supply voltage above 230V. That means that the present situation is analogous to saying something along the lines of "this medicine is 'safe' in at least 40% of the patients who take it" - something which quite obviously would not be regarded as acceptable for most medicines!
Kind Regards, John