I currently have a 6A standard MCB covering the lights in my 1 flat. I'm getting an extractor putinto the bathroom and the electrician says it will take me over this 6A current and that as the wiring is 1.5mm he can fit a 10A RCBO.
I spoke to my dad and he's sure that you can only use 6A for a lighting circuit, so who's right?
Afternoon sarahw.
You appear to understand a fair bit and come on here often so what I would do is buy a copy of the IEE On-site-guide (ISBN 987-0-86341-854-9) which is very easy to understand and will let you find out these things for yourself.
Appendix 1 covers this subject and explains the two factors for lighting circuits.
Current Demand to be Assumed: Current equivalent to the connected load with a minimum of 100W per lampholder. So in your gaff, with 21 spotlights, that would be 2100W.
Amps = Watts/ volts
= 2100 / 230
= 9 Amps
To be safe, to that I would add the current drawn by the fans, on the box, call it x Amps . So current demand to be assumed = 9 + x
Then you apply something called diversity, which is an allowance for not having everything turned on at the same time. With lighting circuits that is 66% of total current demand.
So protective device has to allow
(9 + x ) x 0.66 Amps
As
9 x 0.66 = 6 on it's own then you are correct, quite close.
So that's the theory according to the regs, up to you how you want it putting into practice.