In my opinion it is less than ideal, for circuit end to end identification reason also that documentation will need to state two CSA core sizes.
Plus you will always be calculating on worse case, what if someone decides to now move oven to another location, joins an additional length at the existing oven point via junction box, using 10mm cable?
Gets a little confusing and assumption start to be made, that could lead to dangerous outcomes.
Same CSA for unless discrimination is being offered!
As far as voltage drop that should be addressed at the design stage and I would consider joining two differing core sizes in same circuit, under one protective device not particularly well thought out.
It may well help with Zs reading but if r1 and r2 are sufficient (again design issue) and no external loop problems. Why would you?