It was not 2000 ohms it was 200 last O was the O of Ohms but does not really matter seems the superposition theorem is what I did in Uni under Norton or Thevenin and I remember what a *** it was so I am not going to try working it all out.
It is interesting to see your results. I realise my lash up was just that and one would have to be very unlucky to get a shock and even then unlikely to go permanent damage.
However I still question the idea of using 110 volt portable transformers where 13A outlets to BS7671:2008 are available.
The first time I found a melted 110 volt lead it was blamed on welders not earthing their welding at point of weld.
As I found more and more melted 110 volt cables I and others started to get worried.
So each time it happened we would try to find out why. Normally we just found the discarded cable but then we realised all in one area.
Then we found it. There was a transformer protected with 12 amp push to reset MCB on input and there was a faulty mag mount drill with intermittent short line to earth on the end of two long extension leads.
This would allow something like 50 amps to flow without tripping MCB. And with 1.5mm flex it was melting.
We found quite a few of these transformers on site and quick fix was to use 4 in-line fuse holders with 13A fuses to the two 16A outlets.
But most were hired and it was an impossible task to keep track of what came on and off site.
As time has gone on again and again I have come across problems with 110 volt supplies from US imports with 110-0-110 volt to RCD's opening when generators dropped to idle.
Also where control transformers have been changed from 0-110 volt to 55-0-55 volt and as a result one leg was left unfused not only that unswitched as well. That caused a very expensive burn out.
110 volt if used correctly is a good idea but sorry to say many including electricians don't seem to understand what they have. The continued practice of using brown and blue instead of brown and black as the line wire colours does not help and many fail to switch or fuse the second line feed.
The whole idea of no neutral on a single phase supply seems to be hard for many to grasp. For those who work on three phase it's not so hard to grasp but for people who spend most of their life wiring houses is seems to be something they can't grasp.
The fire risk is high and in spite of sites banning any hand lamps over 60W the fires still happen. Maybe less caused by halogen lamps but the whole idea of flexible cables being viewable throughout there length seems to be forgotten. 413.3.4
I have seen RCD like this
used without too much problem except for dropping out when used with generators so it has been shown they can be made to work in rough conditions and I am sure they could be incorporated within the transformer case. Maybe it will add £39.14 to cost of transformer but that is less than has been added to cost of a consumer unit so what's the problem.
But how can one argue for something to be added because other things maybe wrong?
Same was as caravans are required to have a 30ma RCD fitted in spite of all supplies to caravan also requiring a 30ma RCD and one does not have to be brain of Britain to realise the only time a RCD is required in a caravan is when the site owner has broken the rules.
Of course in the transformer you do not really require a 30ma RCD as it is in the main for fire risk and a 300ma RCD would do the trick. However as yet the regulations do not seem to have allowed for that so we are still stuck with 30ma. Or are we?