crafty1289 said:
120 watts = 10 amps on the low volt side. maybe 1.5mm cable is called for here, but not 6mm
1.5mm² T/E has a V.D. of 29mV/A/m, so if your target is 4% volt drop, 1.5mm² will carry 10A for all of 1.66m
Barney78 said:
So surely there is something seriously wrong with them selling me a kit which has 1mm cable in it when if you put the figures in to the calculator it comes up with 4mm?
Yes - it's not a very good product, but it is not dangerous, which is how they can get away with selling it - the cable can easily carry the current required in complete safety and with a good margin. But why did you think that for some reason nobody would ever sell shoddy electrical items? Why should they be the only products immune from poor design and inadequate performance?
With the results from the cable calculator you are confusing the cable size required to safely carry a given current with the size needed to carry it a given distance without excessive volt drop.
As described, with 1mm² cable, and a 20W load every 0.7m, the voltage present at each of the lamps will be:
11.80
11.59
11.43
11.31
11.23
This means that the last lamp is receiving just under 94% of the nominal 12V. It's probably unlikely that you would notice that, but a 6.4% volt drop is already poor.
If you were to extend the cable by adding 2.5m of 1mm² cable before the first lamp, those voltages would be
11.12
10.93
10.78
10.67
10.59
i.e. the volt drop at the final lamp is 11.75% - far too much.
I don't know where, and by how much you need to lengthen the cable, but your best bet would be to use a short thick piece to a JB, and then individual 1mm² cables, of the same length even if they don't need to be, to each lamp.
Oh - and if you care, once you've modified this kit, it is no longer a CE marked pre-assembled ELV kit, and therefore it is a "special installation" and therefore the law says that you have to notify LABC in advance...