No, it was an isolated incident. I got rid because he swiped 5 of my complection certificates stamped them and sold them for IR£50 (not much more than they cost me to buy (legitimately) in the first place). He was extremely intelligent, (despite his inappropriate use of my megger!) an excellent electrician and would have been finished his industrial apprenticeship within 6mts. He had started cocaine use just before he left. Now in prison for murder. A typical example of such a talent down the drain.
When connected to the ceiling rose the light works when switched on but trips the ring when turned off and back on a second time. The ring is controlled be a MT106 Hager trip switch.
When the light is connected to the normal 13 amp socket is performs without fault, this ring is protected by a MT132 hager trip switch.
What the difference between the two trip switches and is this the cause of the problem.
MT106 is a 6A breaker, MT132 is a 32A one. It sounds like the start-up surge is tripping the 6A one. You could try replacing it with an NC106 (a Type C breaker).