Hi D_Hailsham.
Using Stelrad figures - and interpolating a bit for old non convecting rads, and rounding up here and there:
Ground floor has:
1400x600 single (soon to be double):1372W (soon 2425W)
1600x600 single non conv: 1000W
2800x600 single non conv: 2500W
TOTAL GROUND FLOOR: 4.9kW soon to be 6kW
1st Floor has:
1750x600 single non conv: about 1200W
950x600 single non conv: about 600W
1000x600 double conv: 2kW
Towel rail: say about 700W max?
TOTAL FIRST FLOOR: 4.5kW
Attic conversion has:
1400x400 double conv: 2kW
Towel rail: Say 700W?
TOTAL 2.7kW
House Total: 12kW ish , soon to be 13.2kW
So using your 7kW maximum, the ground floor should be fine on one 15mm circuit, and the other 2 floors on another, with 22mm distribution supplying them from the boiler.
Does that sound right?
If I do run 22mm pipes as per your drawing, do I simply refill and rebalance, or is there technical stuff, adjusting bypass/pump/boiler settings?
Final thought: with the current 15mm circuit, am I simply not getting good performance from the rads and the system as a whole, or am I at risk of knackering the pump/boiler?
Thanks so much for the advice!