The house we bought has 3 lighting circuits with 16A MCBs, most of the loops are done with 2.5mm T+E but I’ve discovered as we’ve been decorating that a lot of the spurs, drops and internal fixture wiring is either 1.5mm or 1mm flex/T&E. This is inherently unsafe right?
The consumer unit is fairly modern, with RCDs and MCBs. A complete re-wire is out of the question right now due to cost, would an interim solution to replace the 16A MCBs with 6A MCBs be a good idea to make these circuits safer?
I‘ve done an audit on the circuits, with the LED bulbs we have fitted everywhere I doubt there is more than 0.5A of demand on any of the individual lighting circuits.
Cheers,
Seb
The consumer unit is fairly modern, with RCDs and MCBs. A complete re-wire is out of the question right now due to cost, would an interim solution to replace the 16A MCBs with 6A MCBs be a good idea to make these circuits safer?
I‘ve done an audit on the circuits, with the LED bulbs we have fitted everywhere I doubt there is more than 0.5A of demand on any of the individual lighting circuits.
Cheers,
Seb