if you plugged in 2 plugs of heavy appliances of 2kw each (say a tumble dryer on full heat, and a 2kw Fan heater) into a double socket wall outlet 2x2kw @240vac = over 16amps - yet a 13amp twin socket outlet is designed to plug in 2x 13a plugs , how is that? there would be a tremendous amount of heat after a while with 16amps ... but its called a 13amp socket even if its a twin socket outlet, not a 26amp socket. - there is not even any failsafe design to the 13a twin socket to dis-allow/disable end users of plugging in 2x2kw (2x8amps) of plugs into a 13amp double socket outlet - let alone some appliances like kettles can use up to 3kw of power.

I'm just curious is all it is.
 
Sponsored Links
There doesn't seem to be any standard specifying the total current rating of a double socket, BS1636 is notablly silent on this point. Howeverit does specify that double sockets should be type tested at a total of 20A, with 6A in one side and 14A in the other. Still this is far short of the maximum possible total that two appliances could draw.

I think the saving graces that stop this being a huge problem in practice are

1. the materials usually used in the UK to make socket outlets and their backboxes are generally pretty resiliant when it comes to overheating. Overheated sockets often turn brown/black or crack, but they don't generally fall apart completely or set themselves on fire.
2. Appliances that draw the full 13A and do so for a long time are relatively uncommon.
 
There doesn't seem to be any standard specifying the total current rating of a double socket, BS1636 is notablly silent on this point. Howeverit does specify that double sockets should be type tested at a total of 20A, with 6A in one side and 14A in the other. Still this is far short of the maximum possible total that two appliances could draw.

I think the saving graces that stop this being a huge problem in practice are

1. the materials usually used in the UK to make socket outlets and their backboxes are generally pretty resiliant when it comes to overheating. Overheated sockets often turn brown/black or crack, but they don't generally fall apart completely or set themselves on fire.
2. Appliances that draw the full 13A and do so for a long time are relatively uncommon.

Is the 2.5mm wiring behind the double 13a socket OK for it? - I see 2.5mm is good for 24amp single phase but does that double to 48amp on a ring circuit? - if you plugged in 2x 3kw appliances that would amount to 25amps wouldn't it? so even if the socket would withstand it what effect would that have on a 2.5mm T&E
 
Is the 2.5mm wiring behind the double 13a socket OK for it? - I see 2.5mm is good for 24amp single phase but does that double to 48amp on a ring circuit? - if you plugged in 2x 3kw appliances that would amount to 25amps wouldn't it? so even if the socket would withstand it what effect would that have on a 2.5mm T&E
2.5mm² T&E has a maximum current carrying capacity of 27A.
 