My F/F is on a non-RCD socket.
If the fridge is faulty this is not normal operation but if it is just tipping the balance then it could be said that it's normal operation and the installation is faulty.314.1 Every installation shall be divided into circuits, as necessary, to:
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation.
543.7.1.1 Equipment having a protective conductor current exceeding 3.5 mA but not exceeding 10 mA, shall be either permanently connected to the fixed wiring of the installation without the use of a plug and socket-outlet or connected by means of a plug and socket-outlet complying with BS EN 60309-2.
Any thoughts on why that is? Although I've never experienced it myself, it seems to be a pretty common complaint.IME, fridges an be b*****r for tripping RCD's.
It is a problem working out what trips an RCD. The 17th Edition states:-
............................................................................................................................................this would be.
If you want any of that, you'll have to rely on transatlantic contributions, since, as you say, there's probably nothing more that any of us could currently say which would help the OP. The OP has already been told that non-compliance with the current regs cannot, per se, explain RCD tripping - and unless/until we are told more about what the report(s) said, there is no more help that can be given. What eric has just written is, indeed, all very reasonable, but I don't think it will help the OP.Nice words Eric and I take it they are for the wider audience. No doubt this will now invite another contributor and/or their American friend to pontificate on the values, aims truths of something or other. ... Because if it aimed at the OP then by their question and answers/non answers they don't really have a clue about the problem they think they have.
Given the extent of difficulties (and time consumed) seemingly often involved in detecting the source of nuisance RCD trips, I'm rather surprised that we do not see (or do not see being used) 'leakage' monitors - or, at least, detectors. I'm sure, for example, that it would be easy enough to produce a relatively cheap plug-in device with a few LEDs which indicated whether L-N imbalance has exceeded certain levels (say 1, 5, 10, 20, 30, 50mA) during the period it had been in circuit. If the OP's electrician had such a device, a definitive answer about the appliance concerned could be achieved very easily. Do any such devices exist?However to test this one would need to monitor the leakage over some 10 hours or ...
Interesting idea, but I'm still not sure how '17th edition compliance' would come into it ...It is possible that manufacturers are aware that the high start up current when a compressor in a fridge or freezer starts can, because of an earth leakage fault elsewhere in the house, cause the RCD to trip. The fridge or freezer is not in itself defective but in connection with something else it is a major contribution to the tripping of the RCD.
IR testing would detect any 'leaks' in the fixed wiring, but I would have thought that by far the majority of 'leaks' (L-E or L-N) are due to equipment/appliances (the testing of which ahs nothing to do with any edition of the Wiring Regs), not fixed wiring. In any event, IR testing was around long before the '17th Edition'.17th edition installations are assumed to have been tested for earth leakage and therefore there is ( should be ) no earth leakage ...
Moeller is the first company with a digital RCD that significantly reduces nuisance tripping and prevents such problems occurring. The digital RCD will always monitor the current system status. If the system's current moves to earth within a range of 0 to 30 percent of the set nominal residual current (IΔN), a green LED will indicate that everything is fine. If the LED changes to yellow this calls for caution, indicating a residual current that is within a range of 30 to 50 percent of the IΔN. This warning means that the level is rising - however the digital RCD does not cause nuicance tripping in this circumstance, but instead indicates that its tripping threshold is being approached. If the LED turns red, the residual current is moving above 50 percent of the IΔN. The system is in a state of alarm and the digital RCD will only trip if the residual current increases beyond 90% of the IΔN.
It's a cop-out.Interesting idea, but I'm still not sure how '17th edition compliance' would come into it ...
Response given in This New ThreadI would agree a residual current monitor (RCM) with recording would be a good tool but I also see some problems. First it would need to be on a non protected circuit and second would need a chart recorder not an every x seconds and join dots like used with current and voltage.
I more-or-less agree. However, I suppose that, at least for some types of equipment (probably not including F/Fs), there is an 'acceptable' (and probably largely unavoidable) low level of leakage which the manufacturer can't really be 'blamed' for. For example, if a PC results in (and is known to result in) a 5mA leakage, I don't think one could take the manufacturer to task because it caused an RCD trip when, say, something else was already resulting in a 27mA leak in the installation.It's a cop-out. ... Because their equipment is producing excessive leakage currents and is therefore tripping an RCD they are saying that the installation is therefore not compliant with 314.1 (iv).Interesting idea, but I'm still not sure how '17th edition compliance' would come into it ...
It may well be a Hotpoint 'cop out' but on the information provided it is difficult to see why you have automatically assumed its their equipment that has caused an RCD problem?It's a cop-out.Interesting idea, but I'm still not sure how '17th edition compliance' would come into it ...
Because their equipment is producing excessive leakage currents and is therefore tripping an RCD they are saying that the installation is therefore not compliant with 314.1 (iv).