Evening,
SGN have replaced the street's gas pipes by feeding a new PE plastic one in through the existing steel pipe. The meter is in cupboard under the stairs. TNCS earthing.
SGN have fitted a new 'electrically insulated' head just before the meter. I have tested and there is no continuity between the steel supply pipe and the consumer's pipework on the other side of the meter. The consumer pipework does not re-enter the ground after this insulated section. Consumer pipework is therefore not extraneous nor require bonding as per 18th ed 411.3.1.2.
That leaves the 20cm of original supply pipe. I have tested and it has resistance of 0.0012 ohms to the MET so is an extraneous conductive part.
When SGN finished, they half taped up this supply pipe in black insulation tape.
Would you:
1) Bond the supply pipe before the meter?
- Disadvantage being it's technically against 544.1.2 as before the meter outlet. And as I can't imagine the neighbours have suddenly switched round their bonding, this steel gas pipe might act as an earth rod for the street should there be a lost neutral. I don't like the idea of the diverted neutral travelling in an old rusty-jointed steel pipe containing plastic and gas.
2) Alternatively, forget bonding and finish wrapping the supply pipe up in tape then wrap again in self-amalgamating tape.
- That way at least no diverted neutral currents would flow down pipe and there is no risk of earth potential if you touch the tape. Disadvantage being the pipe is only safe as long as the tape remains in tact to protect it.
I'm struggling to see how SGN can do this work and potentially leave each house with a 'new' conductive part now isolated from any bonding that might have been present?!
SGN have replaced the street's gas pipes by feeding a new PE plastic one in through the existing steel pipe. The meter is in cupboard under the stairs. TNCS earthing.
SGN have fitted a new 'electrically insulated' head just before the meter. I have tested and there is no continuity between the steel supply pipe and the consumer's pipework on the other side of the meter. The consumer pipework does not re-enter the ground after this insulated section. Consumer pipework is therefore not extraneous nor require bonding as per 18th ed 411.3.1.2.
That leaves the 20cm of original supply pipe. I have tested and it has resistance of 0.0012 ohms to the MET so is an extraneous conductive part.
When SGN finished, they half taped up this supply pipe in black insulation tape.
Would you:
1) Bond the supply pipe before the meter?
- Disadvantage being it's technically against 544.1.2 as before the meter outlet. And as I can't imagine the neighbours have suddenly switched round their bonding, this steel gas pipe might act as an earth rod for the street should there be a lost neutral. I don't like the idea of the diverted neutral travelling in an old rusty-jointed steel pipe containing plastic and gas.
2) Alternatively, forget bonding and finish wrapping the supply pipe up in tape then wrap again in self-amalgamating tape.
- That way at least no diverted neutral currents would flow down pipe and there is no risk of earth potential if you touch the tape. Disadvantage being the pipe is only safe as long as the tape remains in tact to protect it.
I'm struggling to see how SGN can do this work and potentially leave each house with a 'new' conductive part now isolated from any bonding that might have been present?!