OK - so, as I asked in my edit, does that mean that you believe that one should "certainly not" bond any extraneous-c-ps in a TN-C-S installation?I know it's pantomime season, but I'm not playing. I stand by every word I've written.
OK - so, as I asked in my edit, does that mean that you believe that one should "certainly not" bond any extraneous-c-ps in a TN-C-S installation?
Kind Regards, John
How do they get the plastic pipe in the metal pipe?I know it's pantomime season, but I'm not playing.
I stand by every word I've written.
How do they get the plastic pipe in the metal pipe?
Answer: they cut the metal pipe.
There are still some places where metallic service pipes are supplied from metallic street mains.
I knew a gas meter reader who wore insulated gloves when touching meters. This was after he got a muscle jerking shock from a meter.
The "Earth" ( CPC and MET ) in the house were not at Ground potential and as a result the gas meter was not at Ground potential.
There could have been a bond MET to gas meter but there was also the connection via the gas pipe to the CPC "earth" at the gas boiler
Yes correct, where its all steel they are connected together but when changed to plastic that stops happening.the existing steel is chopped up into lots of little pieces to be able to slide the plastic pipe in.
As I've said, in terms of the risk of very high currents flowing in bonding conductors as a result of a fault on the CNE of a TN-C-S supply, "THIS situation" is no different from any other in which one bonds any extraneous-c-p in such an installation.Read exactly what I have said about THIS situation, I stand by every word.
(To be hyper critical) as the pipework is not an extraneous-c-p, it is nothing to do with 411.3.1.2 nor Chapter 54.SGN have fitted a new 'electrically insulated' head just before the meter. I have tested and there is no continuity between the steel supply pipe and the consumer's pipework on the other side of the meter. The consumer pipework does not re-enter the ground after this insulated section. Consumer pipework is therefore not extraneous nor require bonding as per 18th ed 411.3.1.2.
Surely that reading would indicate that the pipe IS main bonded. Very accurate meter?That leaves the 20cm of original supply pipe. I have tested and it has resistance of 0.0012 ohms to the MET so is an extraneous conductive part.
Surely that reading would indicate that the pipe IS main bonded. Very accurate meter?
However, is the insulating section in fact AT the point of entry? If one thinks not then presumably it requires the main bonding.
Is insulating a pipe a recognised alternative for main bonding?
Presumably anyone working on the pipe in the future would prefer it to be bonded (even if they do not understand the principles and would likely bond the wrong pipes with their bonding jumper cable).
I suppose that depends upon how well 'insulated' it is and how 'durable' the insulation is considered to be. If it is considered that the insulation is 'good enough' and likely to remain so, then it is arguably not a 'conductive part' at all, and certainly not "liable to introduce a potential" - so not an extraneous-c-p. If it's not an extraneous-c-p, then it doesn't need bonding. I'm not sure I would personally describe that as 'the insulation being an alternative to main bonding', since it's really a matter of main bonding not being required (if insulation means that the pipe is not an extraneous-c-p).Is insulating a pipe a recognised alternative for main bonding?
They would presumably only prefer it to be bonded if they did not trust the insulation to be, and that it would remain, adequate. In any event, in the OP's case, it's hard to see why anyone would ever need to 'work on' the pipe, which is now seemingly only being used as a conduit for the plastic pipe within it - but if they did do 'work' which involved damaging/destroying the insulation, that would obviously move the goalposts.Presumably anyone working on the pipe in the future would prefer it to be bonded (even if they do not understand the principles and would likely bond the wrong pipes with their bonding jumper cable).
Yes, but we are not talking about that.I suppose that depends upon how well 'insulated' it is and how 'durable' the insulation is considered to be. If it is considered that the insulation is 'good enough' and likely to remain so, then it is arguably not a 'conductive part' at all, and certainly not "liable to introduce a potential" - so not an extraneous-c-p. If it's not an extraneous-c-p, then it doesn't need bonding. I'm not sure I would personally describe that as 'the insulation being an alternative to main bonding', since it's really a matter of main bonding not being required (if insulation means that the pipe is not an extraneous-c-p).
I thought that was the situation - although it could easily still be touched when changing the meter or pipes - but now fjhugh has said "from what I can see the pipe looks to be steel covered in a thick yellow plastic coating for its length under the house until it elbows and comes up." so is it the case that the metal is in fact the supply pipe?They would presumably only prefer it to be bonded if they did not trust the insulation to be, and that it would remain, adequate. In any event, in the OP's case, it's hard to see why anyone would ever need to 'work on' the pipe, which is now seemingly only being used as a conduit for the plastic pipe within it - but if they did do 'work' which involved damaging/destroying the insulation, that would obviously move the goalposts.
Perhaps in this case insulating would be a better alternative to main bonding the supply side?
so is it the case that the metal is in fact the supply pipe?
Oh for heavens sake Sparx I'm only telling what happened in my street and having spoken with others it seems to be what generally happens. But I'm not going to be silly enough to say it's what always happens.Oh no its not, you are guessing and you are wrong, they do not dig up the road to chop up the pipe. They push and pull the plastic as far possible, then they dig a hole - and so on.
Yes correct, where its all steel they are connected together but when changed to plastic that stops happening.the existing steel is chopped up into lots of little pieces to be able to slide the plastic pipe in.