I recently found that our side building is partly wired in 1960's VIR cable (which has no integrated earth continuity), embedded into the cement ceiling and render. The scum who owned the house previously did the trick of replacing the old cable with new where it could be seen, but then hiding junction boxes onto the old cable where they thought it wouldn't be found. There's a light fitting and a socket, on two VIR circuits back to junctions with the appropriate new T&E circuits.
I disconnected the VIR at the junction box that pulling fuses proved to be the correct light circuit, and the light in the side building went off as expected. A voltage detector showed no mains on either the disconnected end or the light fitting end of the VIR. Then I started to disconnect the VIR in the light fitting to replace with a new run of cable... and got a shock when my hand bridged the cable and the earthed metal bulkhead fitting. Checking with a multimeter shows about 1Vac between the red and black, but each has 20Vac to ground. Enough to cause a good buzz.
WTF?
Can anyone offer any insight into this before I proceed? Where on earth (pun intended) is that 20Vac with enough current available to cause a shock coming from?
Edit: I might have a cause... I pulled the fuse on the socket circuit whitch is also junctioned into a (different) run of VIR. The 20Vac went away leaving just 10 to 100 mV as expected on a long cable run near others. Could it be that the light VIR butts up against the socket VIR somewhere (they don't visibly but are embedded into cement so who knows), and the VIR is conductive enough to leak electrons from socket cable to light cable? I can tell you that where I can get to the VIR, it literally crumbles to powder if I wiggle it.
I disconnected the VIR at the junction box that pulling fuses proved to be the correct light circuit, and the light in the side building went off as expected. A voltage detector showed no mains on either the disconnected end or the light fitting end of the VIR. Then I started to disconnect the VIR in the light fitting to replace with a new run of cable... and got a shock when my hand bridged the cable and the earthed metal bulkhead fitting. Checking with a multimeter shows about 1Vac between the red and black, but each has 20Vac to ground. Enough to cause a good buzz.
WTF?
Can anyone offer any insight into this before I proceed? Where on earth (pun intended) is that 20Vac with enough current available to cause a shock coming from?
Edit: I might have a cause... I pulled the fuse on the socket circuit whitch is also junctioned into a (different) run of VIR. The 20Vac went away leaving just 10 to 100 mV as expected on a long cable run near others. Could it be that the light VIR butts up against the socket VIR somewhere (they don't visibly but are embedded into cement so who knows), and the VIR is conductive enough to leak electrons from socket cable to light cable? I can tell you that where I can get to the VIR, it literally crumbles to powder if I wiggle it.