There are many instances of such a circuit being used for a hob and oven where the oven flex requires fusing down.
There are many instances of such a circuit being used for a hob and oven where the oven flex requires fusing down.
No need to embolden things - I read it correctly the first timeThere are many instances of such a circuit being used for a hob and oven where the oven flex requires fusing down.
Fair enough, but ....Ah, but now you have added the part about fault protection. ... You know I never advise not down-fusing on the forum, to which I was referring, as the people will not be able to test it correctly (at all).
You did - but were you not saying (advising?) that the oven flexes should be connected to the outlet without any fusing down, even though the 4mm² circuit may well have been protected by a 32A MCB?I did say in my first reply (in this thread) that I would have just connected both to the outlet.
Not at all. Indeed, if one is concerned about overload protection of the flexes, then his approach would (if it were a 32A circuit, and in the absence of tests of fault protection) theoretically be 'safer' than yours.Do we now presume that the installer did not know what he was doing?
No. DIY advice was not being sought in this thread.You did - but were you not saying (advising?) that the oven flexes should be connected to the outlet without any fusing down, even though the 4mm² circuit may well have been protected by a 32A MCB?
But this was an electrician.Not at all. Indeed, if one is concerned about overload protection of the flexes, then his approach would (if it were a 32A circuit, and in the absence of tests of fault protection) theoretically be 'safer' than yours.Do we now presume that the installer did not know what he was doing?
OK. Fair enough.No. DIY advice was not being sought in this thread. I said that's what I would do.You did - but were you not saying (advising?) that the oven flexes should be connected to the outlet without any fusing down, even though the 4mm² circuit may well have been protected by a 32A MCB?
Perhaps, but I rather doubt it. We've been told that the circuit consists primarily of just 4m of 6mm² cable, so I'd be quite surprised if there were not adequate fault protection for the flex.But this was an electrician. Perhaps he did test and it was not up to fault protection.Not at all. Indeed, if one is concerned about overload protection of the flexes, then his approach would (if it were a 32A circuit, and in the absence of tests of fault protection) theoretically be 'safer' than yours.
Indeed not - but nor, I suspect, would they say that they were limited to a total load of 13A across both 'outlets'.All I can say is MK don't write the BS for 1363 accessories. Lord knows why they wrote that - even they will not endorse the use of two 13A appliances in one of their double sockets...
That's for when there is 'fusing down', but it's downstream (by a maximum of 3m) of the change in CSA. We're talking about no fusing down, when the load is deemed unlikely to cause an overload and the reduced CSA cable has adequate fault (although not overload) protection.Isn't there a 3m rule regarding fusing down?
That certainly makes little sense, at least as a generalisation. Even 1mm² is not OK with a 13A fuse according to BS7671. However, as above, if the load in question were deemed unlikely to result in an overload and IF fault protection of the cable were adequate, then BS7671 would be happy with 0.75mm².Further, manufacturers now fit 13A fuses into plugs connected to 0.75 flex, which is considered safe according to the ESC, but not 7671....
... it's Friday evening and the pubs should be open by now (it's too wet around here, so I'm just going to open my bottle at home!)Je vais prendre mon manteaux...
Ah, that's a bit different from what we thought, and it casts some doubt on whether the electrician was being sensible. You now have 2 ovens, with a total potential load of about 19.2A running off the one 13A fuse in the FCU (the 'fuse and switch' you mention). Theoretically, that is just about OK, since if one applies 'diversity', one is allowed to consider a total cooking appliance load of 19.2A as representing only 12.76A (i.e. fractionally below 13A). However, particularly given that there will be a 13A fuse in the plug for each oven, that additional ('common') 13A fuse it totally unnecessary, and could possible result in problems (occasionally 'blowing'). If you're sticking with the plugs/sockets, the sensible thing would probably be to change that FCU to an (unfused) (probably 40A) switch or, if a switch is not required (i.e. if both socket switches were accessible), just an appropriate junction box.Turns out what I thought was a isolation switch is intact a fcu with a 13 amp fuse and switch. What he has done is taken the cable from the fcu that went to the old oven and attached a dual socket to it.