Could it be simpler to extend the ring, adding another surface mount socket in a convenient location, and running the cable in a length of trunking inbetween?a surface mounted box and socket which protrudes 4cm from the wall
Could it be simpler to extend the ring, adding another surface mount socket in a convenient location, and running the cable in a length of trunking inbetween?a surface mounted box and socket which protrudes 4cm from the wall
I don't think that would be easier. But I'll have a look at the room and consider it!Could it be simpler to extend the ring, adding another surface mount socket in a convenient location, and running the cable in a length of trunking inbetween?
Sort of... plus an appropriately sized flex and a cable gland for the metalclad backbox etc.It sounds like a flex outlet plate with a 26A rated two gang socket, such as the one RandomGrinch links to, would be an acceptable solution?
I reckon max load cwould be a 2KW heater plus a 90w laptop charger...Sort of... plus an appropriately sized flex and a cable gland for the metalclad backbox etc.
....or a cheap extension lead connected to an FCU.
Your choice may depend on your expected loads.
...but that's just my thoughts!
Two gang socket outlets are rated at 20 amps not 26.It sounds like a flex outlet plate with a 26A rated two gang socket, such as the one RandomGrinch links to, would be an acceptable solution?
I've bought 2m of 2.5mm2 3 core. It will be loose, so uninsulated. So should be rated higher than 20A. Haven't checked the on site guide and don't know off the top of my head.In fact the cable is only required to be rated at 20A, though it's also required to be at least 2.5mm² so in favourable installation conditions it's current rating will be significantly higher than 20A.
The implicit assumption is clearly that a double socket is unlikely to be used for two large loads at the same time.
The two cables of the ring, yes (making 40A) - but that does not apply to a spur.In fact the cable is only required to be rated at 20A, though it's also required to be at least 2.5mm² so in favourable installation conditions it's current rating will be significantly higher than 20A.
Why?The implicit assumption is clearly that a double socket is unlikely to be used for two large loads at the same time.