watts = volts times amps
amps = watts divided by volts
X = 6000 / 230 = 26
So both heaters on the same 20 amp radial will be OVERLOAD
Two radials at 20 Amps or a ring at 32 amp. Do NOT plug the two heaters into a twin socket. Use separate single sockets.
why wouldnt you use just one twin socket?
is it ok to use a fused spur with a 13amp fuse in it? as the heaters have no plugs.
why wouldnt you use just one twin socket?
Because many are not rated at 26 amps load even though they have two "13 amp" sockets. The terminals and metal connections cannot take 26 amps
is it ok to use a fused spur with a 13amp fuse in it? as the heaters have no plugs.
Probably.
Your apparent lack of knowledge about how many amps the heaters will take suggests this is work beyond you ability and knowledge to do safely as a DIY project. Strongly suggest you consult an electrician.
Your electrician can get the materials cheaper and quicker. And will make the decision as to what materials to use.
Your electrician can get the materials cheaper and quicker. And will make the decision as to what materials to use.
Thats ok,
but could somebody just say so that in my head i know ruffly whats going on,
is fused spurs ok with 13amp fuses yea? with 20amp breakers and 4mm t+e?
so is 4mm2 cable and 2 fused spurs ok for the job with 2x 20amp breakers yea??
Thanks.
It's the pizza oven shambles all over again.Hang on, aren't you the guy who's supposedly an apprentice yet doesn't know what an RCD is?
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local