Why would you think that?
Hospitals began using their own (rather dangerous) design of round pin plug - where the live pin was the replaceable fuse.
In my experience the red plugs are used as a 'Do not remove' sign.I seem to recall Red mk plugs with For Gpo Use stamped on them, or am i dreaming
Fit a brand new plug and see if it is any better.
It does seem the 13 amp plug has been down graded, the necking of the live pins to put plastic sleeves on them has reduced the ability to transfer heat away from the fuse, black plugs are better than white, and clearly need to be in free air, the whole design of the ring final and 13 amp plug during the war was with the idea of powering heaters, so they should be OK, and with a thermostatic controlled oil filled radiator I have not had a problem, but 3 kW does seem today to be two much as a continuous rating. So as to if 20A switch or 13A fused spur depends what feeds it, from a ring final would need to be fused spur and with the down grading of cable from 7/0.029 (2.9 mm²) to 2.5 mm² one needs to be careful drawing over 2 kW from a ring final, OK near the centre but near the consumer unit can cause one leg to be over loaded.
The IET BS 7671 now warns of the problem with over 2 kW fixed appliances and suggests over 2 kW should have a dedicated supply, which we have done for years with the immersion heater, but do not tend to have done with tumble drier or washer drier, there has been a move to 2 kW for cloths drying, but it means the answer to your question in not cut and dried due to the down grading of the ring final.
Least we forget the ring final was designed during the war to assist with the rebuilding they realised would be required post war, and the shortage of copper. It does seem a FCU can dissipate the heat from the fuse better than a plug.
The regulation which 'dispensates' ring final circuits requires the cable only to have a minimum CCC of 20A.How exactly can you overload just one leg of a ring, when the ring is fed from two ways?
How exactly can you overload just one leg of a ring, when the ring is fed from two ways?
Do you see any advantage in that method over having a radial circuit?One way, where the ring circuit is all in a straight line along a wall, is to use 'alternate wiring' for sockets. Call the two runs out and back A and B, first socket along the wall connected to A, second socket connected to B, followed by A then B all the way to the far end.
Certainly it does not save copperDo you see any advantage in that method over having a radial circuit?
I'm not really sure how that would help anything. It remains the case that the theoretical risk of somewhat 'overloading' one arm of the ring will exist if something approaching 32A worth of loads is connected to sockets close (electrically) to one end of the ring, and that is regardless of where the sockets are physically located.One way, where the ring circuit is all in a straight line along a wall, is to use 'alternate wiring' for sockets. Call the two runs out and back A and B, first socket along the wall connected to A, second socket connected to B, followed by A then B all the way to the far end.
Indeed, if someone wanted to avoid that theoretical/hypothetical risk by avoiding plugging several large loads into sockets which were (electrically) close to one end of the ring, what you suggest would make life more difficult for them, because they could not so easily deduce which of the sockets were (electrically) close to (the same) one end of the ring!
it's a good point.I'm not really sure how that would help anything. It remains the case that the theoretical risk of somewhat 'overloading' one arm of the ring will exist if something approaching 32A worth of loads is connected to sockets close (electrically) to one end of the ring, and that is regardless of where the sockets are physically located.
Indeed, if someone wanted to avoid that theoretical/hypothetical risk by avoiding plugging several large loads into sockets which were (electrically) close to one end of the ring, what you suggest would make life more difficult for them, because they could not so easily deduce which of the sockets were (electrically) close to (the same) one end of the ring!
Kind Regards, John.
Do you see any advantage in that method over having a radial circuit?