Hello, I'm not sure whether to get a 24kW or 30kW combi boiler for a flat (only £10 difference)
The 30kW boiler would only just be OK for the size of gas pipe that can fit in the building - if I've worked it out correctly.
Please can someone advise on getting a 24kW boiler in a small 2 bed flat, or 30kW for a good flow rate on thermostatic showers?
If anyone has time to check heres my calculation for the 30kW boiler:
30kWh boiler stated 3.12 m3/h max flow rate = 0.0008666667m3/s
From CIBSE tables: http://www.cibse.org/getmedia/b7008...025a/Guide-C-2001-Natural-gas-tables.pdf.aspx
22mm 5.5 Pa pressure drop per meter
28mm 1.5 Pa pressure drop per meter
From meter - 28mm for 11.5m, 6no. Elbows - 3m, Total length: 14.5m x 1.5 = 21.75 Pa pressure drop (first part)
Reduce to 22mm for 10m, 5no. Elbows - 2.5m, Total length: 12.5m x 5.5 = 68.75 Pa pressure drop (second part)
Total pressure drop = 90.5 Pa = 0.905 mbar
The 28mm pipe can't be any longer as it won't fit in the building neatly.
Is a theoretical drop of 0.905mbar too close to the limit? Should I just get the 24kw?
Need to make a decision on the boiler soon. However building won't be ready till March so it seems too early to get quotes and ask these questions.
Thank you for reading this far!
The 30kW boiler would only just be OK for the size of gas pipe that can fit in the building - if I've worked it out correctly.
Please can someone advise on getting a 24kW boiler in a small 2 bed flat, or 30kW for a good flow rate on thermostatic showers?
If anyone has time to check heres my calculation for the 30kW boiler:
30kWh boiler stated 3.12 m3/h max flow rate = 0.0008666667m3/s
From CIBSE tables: http://www.cibse.org/getmedia/b7008...025a/Guide-C-2001-Natural-gas-tables.pdf.aspx
22mm 5.5 Pa pressure drop per meter
28mm 1.5 Pa pressure drop per meter
From meter - 28mm for 11.5m, 6no. Elbows - 3m, Total length: 14.5m x 1.5 = 21.75 Pa pressure drop (first part)
Reduce to 22mm for 10m, 5no. Elbows - 2.5m, Total length: 12.5m x 5.5 = 68.75 Pa pressure drop (second part)
Total pressure drop = 90.5 Pa = 0.905 mbar
The 28mm pipe can't be any longer as it won't fit in the building neatly.
Is a theoretical drop of 0.905mbar too close to the limit? Should I just get the 24kw?
Need to make a decision on the boiler soon. However building won't be ready till March so it seems too early to get quotes and ask these questions.
Thank you for reading this far!