Just wanted to confirm my understanding here.
Ignoring power factor for the moment, I know that the formula used to get current from total power is total power/(root 3 x phase voltage)
This is the phase current, so we use this for each line cable and fuse, of which there'll be 3.
The root 3 part confused me a bit, as it seems to give a voltage of 692.8, but as the line voltage is 230v, the phase voltage is root 3 times, or 400v.
Another way to look at it is total power/line voltage. Gives total current. So phase current will be one third.
So a 9kw heater, 400v 3 phase will have a total current of 9000/230 = 39.19A spread across 3 phases so each line cable carries one third or 13.04A.
9000/(root 3 * 400) gives the line current too. 9000/692.8 = 12.99A