Hi Everyone
I have spent the last 2 days reading Diagrams and watching YouTube videos on Y plan systems and 3 port valves but I have not found any that have shown the problem I had which was that the Boiler got stuck on (pump running and heat circulation) making the hot water cylinder and rads hotter and hotter after turning the boiler off for a few hours then turning it back on and testing both the stats and Drayton control panel everything worked as normal this problem has happened before so I replaced the CH stat and Drayton control panel assuming that one of these was the culprit the Drayton panel did have a sticky relay but Now the problem has happened again I have focused on the 3 port valve and cylinder stat I feel the issue is with the 3 port valve as I-am told this is the first thing heating Engineers replace when this sort of problem happens.
Anyway The problem I had was that the CH thermostat was satisfied ,the HW Cylinder stat was satisfied and the Drayton control panel relays both HW and CH side were off (not calling) therefore after studying videos and drawings I can only conclude that the the diode in the 3 port valve somehow malfunctioned allowing the Grey wire which is permanently live to short over to the Orange one which fires up the boiler this would in my opinion explain the boiler going into a kind of run away mode. What I want to know is that is this a possibility? Otherwise I cant see anywhere else as to where the boiler could have been getting a live trigger from then held into a kind of run away mode?
I have spent the last 2 days reading Diagrams and watching YouTube videos on Y plan systems and 3 port valves but I have not found any that have shown the problem I had which was that the Boiler got stuck on (pump running and heat circulation) making the hot water cylinder and rads hotter and hotter after turning the boiler off for a few hours then turning it back on and testing both the stats and Drayton control panel everything worked as normal this problem has happened before so I replaced the CH stat and Drayton control panel assuming that one of these was the culprit the Drayton panel did have a sticky relay but Now the problem has happened again I have focused on the 3 port valve and cylinder stat I feel the issue is with the 3 port valve as I-am told this is the first thing heating Engineers replace when this sort of problem happens.
Anyway The problem I had was that the CH thermostat was satisfied ,the HW Cylinder stat was satisfied and the Drayton control panel relays both HW and CH side were off (not calling) therefore after studying videos and drawings I can only conclude that the the diode in the 3 port valve somehow malfunctioned allowing the Grey wire which is permanently live to short over to the Orange one which fires up the boiler this would in my opinion explain the boiler going into a kind of run away mode. What I want to know is that is this a possibility? Otherwise I cant see anywhere else as to where the boiler could have been getting a live trigger from then held into a kind of run away mode?